I'll admit I'm a bit rusty on sizing, I use my yellow code manual and rules of thumb I learned from electricians who helped me out over the years. I typically use 750w/hp for motors, which would be 2250w for 3hp. @200v that's about 10A. I believe the FLA is the max amperage before the motor can take when voltage drops -- so draw 14A the line voltage would have to drop below 160VAC.Thanks for the link.
Motor is marathon d013. 3 hp. 14 fla.
OK, so you're looking at 2 things, conductor size and breakers. Your conductors must take 1.25 the ampacity of FLA, or 17.5A which is within the technical limit of NMD90 14ga, however, I think most electricians would spec 12 ga. The breaker should not exceed the limit of the conductor, which I'd set at 20A.
Ampacity Chart | Wire & Cable Technical Resources | Lapp Tannehill - this is a nice chart. Typically we use 90C l(NMD90), so you 14AWG will handle up to 25A).